口袋微信抓娃娃源码不能微信登录?为什么没有微信登录了???

怎么备份和恢复SE6.0工程?我是指分布式应用,不是单机?
>> 怎么备份和恢复SE6.0工程?我是指分布式应用,不是单机?
怎么备份和恢复SE6.0工程?我是指分布式应用,不是单机?
tianjichun, 23:30:53
[FACE=宋体][SIZE=14px]Factory Talk view SE 6.0分布式应用,在studio里面把整个项目备份后称***.bak,但找不到恢复的办法,请各位赐教,怎么备份和恢复SE6.0工程?[/SIZE][/FACE]玻璃杯, 06:54:26
Question How do I backup a FactoryTalk View SE Application before moving it to a new PC?
How do I move or copy FactoryTalk View SE Application to a new PC?
How do I recover FactoryTalk View SE .apa backup file running in a new PC?
How to back up and restore a FactoryTalk Directory (Local and Network)?
Environment FactoryTalk View Site Edition Networks and Local Application
Answer Network Application Before moving FactoryTalk View to a new PC, you must backup the structure or layout of the application. The steps below backup the application name, area names, data server and shortcut names, as well as the Tag Alarm and Event Server (if in use). The FactoryTalk directory and connections are not backed up unless you check the box toBackup the System Archive.
Step I - Backup FactoryTalk Information 1. Start the FactoryTalk Administration Console. Go to Windows Taskbar--&Start--& Programs--& Rockwell Software--& FactoryTalk Administration Console. Select Network, if prompted. 2. In the Explorer tree on the left, right-click on your application and select Backup.
Note: If you checkBackup System Archive, you also backup the FactoryTalk Directory, which is everything below the System folder in the Explorer tree.
3. Note the name and location where the backup file (.bak) will be stored and select OK. 4. If you are using a Tag Alarm and Event Server in your application, export the tags to an Excel file by right-clicking on the Tag Alarm and Event Server and selecting Import and Export. Follow the prompts.
Step II - Backup the HMI Application Before you can backup the HMI application, you must download the RSView SE - Backup and Restore Utility for HMI Server. For instructions on downloading the RSView SE - Backup and Restore Utility for HMI Server, refer to AID 30310. Install and register this application as a service and your backup application.
Note: Version 5.1 of FactoryTalk View Site Edition and above comes with a newer version of the HMI Backup Utility called HMI Server Backup and Restore This utility is located in Programs--&Rockwell Software--&FactoryTalk View--&Tools. Use this version for the 5.1 release.
Check the size of the tag database file after the backup is performed. If it is 201 KBytes and you have tags in the database there is a chance that the backup is bad. Try running the HMI Backup again when the server is not busy (when less clients are connected). The Tag Database is located in the Tag folder and will have a .DB extension or .MDF (for ver. 6.1 and above) extension.
Step III - Backup OPC Server Backup the configuration for RSLinx Classic or the 3rd party OPC server if you are using one. For RSLinx Classic, use the RSLinx Classic Backup and Restore Utility. For other OPC servers, check your documentation.
Step IV - Moving the Application to a different PC 1. On the new PC, copy all backed-up files, including the HMI application, to a local folder.
2. Start the FactoryTalk Administration Console. Go to Windows Taskbar--&Start--&Programs--&Rockwell Software--&FactoryTalk Administration Console. Select Network, if prompted.
3. At the top of the Explorer tree on the left, right-click on Network and select Restore. 4. Browse to the archive to restore (the .bak file). Select Next. 5. Uncheck the Restore System checkbox, if checked, unless you also want to restore the FactoryTalk directory from the backup. Leave the box checked if you want to restore the application and give it a new name. If you just want to restore the application and keep the same name, leave both boxes unchecked.
Note: If you restore the System, the current FactoryTalk directory is replaced, which also includes usernames and passwords as well as policies and connections. In other words, everything below the System folder in the Explorer tree on the left is over written.
Once the Application is restored, expand your application in the Explorer tree. Right-click on the data server and select Properties. Browse to the PC that will be hosting the data server.
Note: If using RSLinx Enterprise, check your shortcuts and make sure they are linked to the correct processor. If using RSLinx Classic or a 3rd party OPC server, point it to the correct PC and restore the configuration or the OPC server that you are using.
6. If using a Tag Alarm and Event Server, right-click on it and select Properties. Select the computer hosting the server. If you exported the tags as specified in section 1 above, import them by right-clicking on the Tag Alarm and Event Server and selecting Import and Export. Follow the prompts. 7. Close the FactoryTalk Administration console. 8. From the Windows Taskbar, right-click on Start and select Explore All Users. Go to Documents and Settings--&All Users--&Documents--&RSView Enterprise--&SE\HMI Projects. 9. You can use the HMI Backup Utility to restore the application to the HMI Projects folder if the project already exists or if the project does not exist you can manually copy the backed up HMI Project into the HMI Projects folder. If the HMI server will not open in Studio after the backup is restored. You can remove it from the HMI Projects folder, then open the project in Studio. The HMI server will have a red stop circle by it. Note the name of it and delete it. Then create a new HMI server with the same name and import the backed up project. 10. Reboot the PC. 11. Start up FactoryTalk View SE and open the application. Repoint the HMI server to the host PC. Right-click on the HMI Server and select Properties. 12. Browse to the Computer hosting the server. 13. If you have Datalog Models setup, open the models and make sure the path is setup correctly. Local or Standalone Application 1. To backup and restore a local or standalone application, use the Application Manager. This utility is located in Programs--&Rockwell Software--&FactoryTalk View--&Tools 2. The Application Manager creates an .apa file 3. Copy the .apa file into new PC 4. Restore the application using the Application Manager. 5. You have the option to restore the SE Local Application or the Local Application and Local FactoryTalk Directory. If you restore the local FactoryTalk Directory, the current Local FactoryTalk Directory on the PC is overwritten. 6. A reboot is required after the restore. 7. To run this application, make sure FactoryTalk View SE Station license is installed, and configure FactoryTalk View SE client to run it.dxtkcsm, 08:27:41
用FactoryTalk Administration Console备份和恢复tianjichun, 16:12:09
谢谢,感觉RSVIEW SE 分布试项目备份和恢复很复杂和麻烦,单机还可以,很简单的就备份和恢复了 。不像其他软件,我使用CITECT时,比这个灵活的多。就没有其他高手说说,还有其他简单,可行的方法吗?&97
8: 此主题共有4帖 此页4帖 每页12帖&怎么备份和恢复SE6.0工程?我是指分布式应用,不是单机? - 中国亿万电器网 - Powered by LeadBBS 6.0
loading...
loading...
+1魅力1积分1248经验19118文章230注册
怎么备份和恢复SE6.0工程?我是指分布式应用,不是单机?
[FACE=宋体][SIZE=14px]Factory Talk view SE 6.0分布式应用,在studio里面把整个项目备份后称***.bak,但找不到恢复的办法,请各位赐教,怎么备份和恢复SE6.0工程?[/SIZE][/FACE]
+548魅力548积分5858经验51629文章1813注册
Question How do I backup a FactoryTalk View SE Application before moving it to a new PC?
How do I move or copy FactoryTalk View SE Application to a new PC?
How do I recover FactoryTalk View SE .apa backup file running in a new PC?
How to back up and restore a FactoryTalk Directory (Local and Network)?
Environment FactoryTalk View Site Edition Networks and Local Application
Answer Network Application Before moving FactoryTalk View to a new PC, you must backup the structure or layout of the application. The steps below backup the application name, area names, data server and shortcut names, as well as the Tag Alarm and Event Server (if in use). The FactoryTalk directory and connections are not backed up unless you check the box toBackup the System Archive.
Step I - Backup FactoryTalk Information 1. Start the FactoryTalk Administration Console. Go to Windows Taskbar--&Start--& Programs--& Rockwell Software--& FactoryTalk Administration Console. Select Network, if prompted. 2. In the Explorer tree on the left, right-click on your application and select Backup.
Note: If you checkBackup System Archive, you also backup the FactoryTalk Directory, which is everything below the System folder in the Explorer tree.
3. Note the name and location where the backup file (.bak) will be stored and select OK. 4. If you are using a Tag Alarm and Event Server in your application, export the tags to an Excel file by right-clicking on the Tag Alarm and Event Server and selecting Import and Export. Follow the prompts.
Step II - Backup the HMI Application Before you can backup the HMI application, you must download the RSView SE - Backup and Restore Utility for HMI Server. For instructions on downloading the RSView SE - Backup and Restore Utility for HMI Server, refer to AID 30310. Install and register this application as a service and your backup application.
Note: Version 5.1 of FactoryTalk View Site Edition and above comes with a newer version of the HMI Backup Utility called HMI Server Backup and Restore This utility is located in Programs--&Rockwell Software--&FactoryTalk View--&Tools. Use this version for the 5.1 release.
Check the size of the tag database file after the backup is performed. If it is 201 KBytes and you have tags in the database there is a chance that the backup is bad. Try running the HMI Backup again when the server is not busy (when less clients are connected). The Tag Database is located in the Tag folder and will have a .DB extension or .MDF (for ver. 6.1 and above) extension.
Step III - Backup OPC Server Backup the configuration for RSLinx Classic or the 3rd party OPC server if you are using one. For RSLinx Classic, use the RSLinx Classic Backup and Restore Utility. For other OPC servers, check your documentation.
Step IV - Moving the Application to a different PC 1. On the new PC, copy all backed-up files, including the HMI application, to a local folder.
2. Start the FactoryTalk Administration Console. Go to Windows Taskbar--&Start--&Programs--&Rockwell Software--&FactoryTalk Administration Console. Select Network, if prompted.
3. At the top of the Explorer tree on the left, right-click on Network and select Restore. 4. Browse to the archive to restore (the .bak file). Select Next. 5. Uncheck the Restore System checkbox, if checked, unless you also want to restore the FactoryTalk directory from the backup. Leave the box checked if you want to restore the application and give it a new name. If you just want to restore the application and keep the same name, leave both boxes unchecked.
Note: If you restore the System, the current FactoryTalk directory is replaced, which also includes usernames and passwords as well as policies and connections. In other words, everything below the System folder in the Explorer tree on the left is over written.
Once the Application is restored, expand your application in the Explorer tree. Right-click on the data server and select Properties. Browse to the PC that will be hosting the data server.
Note: If using RSLinx Enterprise, check your shortcuts and make sure they are linked to the correct processor. If using RSLinx Classic or a 3rd party OPC server, point it to the correct PC and restore the configuration or the OPC server that you are using.
6. If using a Tag Alarm and Event Server, right-click on it and select Properties. Select the computer hosting the server. If you exported the tags as specified in section 1 above, import them by right-clicking on the Tag Alarm and Event Server and selecting Import and Export. Follow the prompts. 7. Close the FactoryTalk Administration console. 8. From the Windows Taskbar, right-click on Start and select Explore All Users. Go to Documents and Settings--&All Users--&Documents--&RSView Enterprise--&SE\HMI Projects. 9. You can use the HMI Backup Utility to restore the application to the HMI Projects folder if the project already exists or if the project does not exist you can manually copy the backed up HMI Project into the HMI Projects folder. If the HMI server will not open in Studio after the backup is restored. You can remove it from the HMI Projects folder, then open the project in Studio. The HMI server will have a red stop circle by it. Note the name of it and delete it. Then create a new HMI server with the same name and import the backed up project. 10. Reboot the PC. 11. Start up FactoryTalk View SE and open the application. Repoint the HMI server to the host PC. Right-click on the HMI Server and select Properties. 12. Browse to the Computer hosting the server. 13. If you have Datalog Models setup, open the models and make sure the path is setup correctly. Local or Standalone Application 1. To backup and restore a local or standalone application, use the Application Manager. This utility is located in Programs--&Rockwell Software--&FactoryTalk View--&Tools 2. The Application Manager creates an .apa file 3. Copy the .apa file into new PC 4. Restore the application using the Application Manager. 5. You have the option to restore the SE Local Application or the Local Application and Local FactoryTalk Directory. If you restore the local FactoryTalk Directory, the current Local FactoryTalk Directory on the PC is overwritten. 6. A reboot is required after the restore. 7. To run this application, make sure FactoryTalk View SE Station license is installed, and configure FactoryTalk View SE client to run it.Do it others will not!
-3积分8304经验148534文章2743注册
用FactoryTalk Administration Console备份和恢复
+1魅力1积分1248经验19118文章230注册
谢谢,感觉RSVIEW SE 分布试项目备份和恢复很复杂和麻烦,单机还可以,很简单的就备份和恢复了 。不像其他软件,我使用CITECT时,比这个灵活的多。就没有其他高手说说,还有其他简单,可行的方法吗?
loading...
loading...
loading...
loading...
loading...
loading...
长度不得超过255字
内容(最大25K)
是否是UBB代码
Alt+S或Ctrl+Enter快速提交
Powered by .求助:SE备份工程文件,可是没有备份或者恢复的选项 - 中国亿万电器网 - Powered by LeadBBS 6.0
loading...
loading...
+1魅力1积分248经验2067文章6注册
求助:SE备份工程文件,可是没有备份或者恢复的选项
问题描述:
我要备份我的工程文件(network类型),使用Application Manager;可是根本没有backup或者restore的选项!
请问是什么原因?
问题如图…
[upload=76664,0]QQ图片42.jpg[/upload]
[upload=76665,0]QQ图片20.jpg[/upload]
职务论坛版主声望+1815魅力1713积分20994经验182967文章5745注册
是不是重名了?auto_
工控技术交流QQ千人群:(满员)
工控交流群三群,群号码:
+1魅力1积分248经验2067文章6注册
[QUOTE][b]下面引用由[u]guolibin[/u]发表的内容:[/b]
是不是重名了?[/QUOTE]
不是重名,按照正常步骤,应该是点击了SE(network)下一步,选择backup,然后再选择工程文件……
现在连backup的选项都没有
+1魅力1积分39经验569文章5注册
[FACE=Arial, Helvetica, sans-serif][COLOR=rgb(50, 50, 50)][SIZE=14px]SE 新建工程时有四种类型可选,如果是Network Distributed 类型,是不可以用Application Manager 进行备份的[/SIZE][/COLOR][/FACE]
+39魅力39积分290经验2149文章73注册
这是不是你的软件的啊问题啊,我这可都有的啊,一直有
+124魅力124积分704经验3778文章56注册
网络的备份就是没有的
935经验11174文章148注册
用application manager,对于网络的应用程序,只能删除和重名应用程序。如果是SE6.0以上,可以用自带的HMI server backup and restore工具进行备份还原。
-3积分8304经验148534文章2743注册
FactoryTalk Administration Console
+1魅力1积分163经验1550文章9注册
软件版本太老了
+119魅力119积分1295经验11279文章72注册
[QUOTE][b]下面引用由[u]潇狼gcs[/u]发表的内容:[/b]
SE 新建工程时有四种类型可选,如果是Network Distributed 类型,是不可以用Application Manager 进行备份的[/QUOTE]
这位说的对!
loading...
loading...
loading...
loading...
loading...
loading...
长度不得超过255字
内容(最大25K)
是否是UBB代码
Alt+S或Ctrl+Enter快速提交
Powered by .求助:SE备份工程文件,可是没有备份或者恢复的选项 - 中国亿万电器网 - Powered by LeadBBS 6.0
loading...
loading...
+1魅力1积分248经验2067文章6注册
求助:SE备份工程文件,可是没有备份或者恢复的选项
问题描述:
我要备份我的工程文件(network类型),使用Application Manager;可是根本没有backup或者restore的选项!
请问是什么原因?
问题如图…
[upload=76664,0]QQ图片42.jpg[/upload]
[upload=76665,0]QQ图片20.jpg[/upload]
职务论坛版主声望+1815魅力1713积分20994经验182967文章5745注册
是不是重名了?auto_
工控技术交流QQ千人群:(满员)
工控交流群三群,群号码:
+1魅力1积分248经验2067文章6注册
[QUOTE][b]下面引用由[u]guolibin[/u]发表的内容:[/b]
是不是重名了?[/QUOTE]
不是重名,按照正常步骤,应该是点击了SE(network)下一步,选择backup,然后再选择工程文件……
现在连backup的选项都没有
+1魅力1积分39经验569文章5注册
[FACE=Arial, Helvetica, sans-serif][COLOR=rgb(50, 50, 50)][SIZE=14px]SE 新建工程时有四种类型可选,如果是Network Distributed 类型,是不可以用Application Manager 进行备份的[/SIZE][/COLOR][/FACE]
+39魅力39积分290经验2149文章73注册
这是不是你的软件的啊问题啊,我这可都有的啊,一直有
+124魅力124积分704经验3778文章56注册
网络的备份就是没有的
935经验11174文章148注册
用application manager,对于网络的应用程序,只能删除和重名应用程序。如果是SE6.0以上,可以用自带的HMI server backup and restore工具进行备份还原。
-3积分8304经验148534文章2743注册
FactoryTalk Administration Console
+1魅力1积分163经验1550文章9注册
软件版本太老了
+119魅力119积分1295经验11279文章72注册
[QUOTE][b]下面引用由[u]潇狼gcs[/u]发表的内容:[/b]
SE 新建工程时有四种类型可选,如果是Network Distributed 类型,是不可以用Application Manager 进行备份的[/QUOTE]
这位说的对!